What size/ type of inline fusing should I use between the PV panel and the controller and the controller and the 12V battery?
|
|
|
Fuses
Apr 30, 2019 23:07:42 GMT
Post by tattoo on Apr 30, 2019 23:07:42 GMT
It depends on how many panels you have and what size CC you have...... Way more info needed to accurately answer your question.....
|
|
|
Fuses
Apr 30, 2019 23:10:35 GMT
Post by john on Apr 30, 2019 23:10:35 GMT
one 100W panel and Adventurer controller
|
|
|
Fuses
May 1, 2019 0:20:57 GMT
Post by bupkis on May 1, 2019 0:20:57 GMT
I would not fuse the panel/controller side. Fusing the controller/battery side to 10 or 15A assuming you wires are large enough for 10-15A (the should be).
|
|
|
Fuses
May 1, 2019 2:07:29 GMT
Post by tattoo on May 1, 2019 2:07:29 GMT
Yes sir that's correct..... It really helps when you can ask a question and get an answer.........
|
|
|
Fuses
May 6, 2019 23:30:15 GMT
Post by Admin on May 6, 2019 23:30:15 GMT
What size/ type of inline fusing should I use between the PV panel and the controller and the controller and the 12V battery? 7-10A is appropriate for panel to controller, and 30A is normally what we recommend for the controller, assuming you would be expanding. -Renogy Team
|
|