Post by bupkis on Sept 2, 2018 16:52:01 GMT
|
|
|
Post by tattoo on Sept 2, 2018 17:10:44 GMT
Yea I have one of them, It was with my 40aCC.... Or still is, I still have it...
|
|
|
Post by Admin on Sept 2, 2018 17:34:39 GMT
change nothing if you believe your hydrometer. manual shows 14.8v eq / 14.6v charge, not much different and not likely to mess up anything!!! Consider the mt remote display! The MT-50 is compatible with the Commander 20 and Commander 40, not the Commander 60. The Commander 60 has the PC software compatibility. -Renogy Team
|
|
|
Post by tattoo on Sept 2, 2018 19:59:21 GMT
Yep that's right LOL I forgot since I don't use a remote device.... But I might consider it...
The 60a CC has all the info that I have been given on the screen itself just like the MT50 displays and even more after thinking about it...
|
|
|
Post by tattoo on Sept 2, 2018 22:31:43 GMT
Well no float today either..... The batteries did get up to 14.9 at some point today but not long enough I guess....
I did see 41.8a coming from the panels at one point....
Well lets see what tomorrow brings with the Eq.... I'm planning on turning off all on my load as suggested tomorrow for three hours to see what happens... Just to cut out any chances of a glitch on my end...
|
|
|
Post by tattoo on Sept 3, 2018 23:37:30 GMT
Ok While I was waiting the Sun to get over head I decided to go through the settings on my 60a CC... Man this thing does way more than I remembered...Mainly because I hadn't needed to get back into it......
Here are some of the things I found on it... I guess you can change the settings but I'm not changing anything for now...
|
|
|
Post by tattoo on Sept 3, 2018 23:39:29 GMT
Here are a couple more... And there were more but it covered what I'm working on right now... Attachments:
|
|
|
Post by tattoo on Sept 3, 2018 23:42:34 GMT
Ok these pics are from the beginning when I unhooked all of the load on the system and the panels are in full sun...
|
|
|
Post by tattoo on Sept 3, 2018 23:43:50 GMT
Ok here are a few more of the start......
|
|
|
Post by tattoo on Sept 3, 2018 23:45:06 GMT
Ok one more pic in this..... Attachments:
|
|
|
Post by tattoo on Sept 3, 2018 23:46:32 GMT
Now these pics are from an hour later, We did have a little bit of clouds today blowing over but nothing that kept the panels without Sun for more than 3 min....
|
|
|
Post by tattoo on Sept 3, 2018 23:49:37 GMT
One more pic..... Attachments:
|
|
|
Post by tattoo on Sept 3, 2018 23:57:56 GMT
Ok how do you think the CC is doing so far?? I figured pics are much better than me telling you how they are doing and it's also showing it in real time...
Now that I'm doing this in depth way more than I've ever done it's very interesting and eye opening...
|
|
|
Post by bupkis on Sept 4, 2018 11:03:55 GMT
PV voltage 61 rising to 70v indicates to me the cc is in regulation as designed.
I'd expect in the next hr that PV voltage would rise further, current/power to decline (from regulation and the sun), followed by Float.
|
|
|
Post by tattoo on Sept 4, 2018 12:44:35 GMT
PV voltage 61 rising to 70v indicates to me the cc is in regulation as designed. I'd expect in the next hr that PV voltage would rise further, current/power to decline (from regulation and the sun), followed by Float. Yes sir you would think that.... By the way I never took any pics when it was cloudy all were in full sun light...
|
|