Post by JP4Guzzler2 on Mar 10, 2019 17:26:10 GMT
Hello, I'm wondering if I have a bad controller. Measured open voltage on the panel leads is 43 volts. When attached to controller voltage always reads battery voltage 12-13v. Panels symbol shows daylight and moon symbols but never turns on panel charge light or records charge amp hours, ever. Time to call service?
|
|
|
Post by JP4Guzzler2 on Mar 10, 2019 17:28:11 GMT
Rover 40 MPPT with 3X 100w in series
|
|
|
Post by tattoo on Mar 10, 2019 21:26:04 GMT
How old is your CC??
It sounds like it's bad to me....
|
|
|
Post by jp4guzzler on Mar 10, 2019 21:44:54 GMT
30 days old
|
|
|
Post by tattoo on Mar 11, 2019 2:24:42 GMT
WOW I've heard of them going bad that quick....
But, Has it ever worked correctly?
|
|
|
Post by tattoo on Mar 11, 2019 2:26:34 GMT
I believe you have your + and - crossed from your panels to the CC..... If it has never worked right...
|
|
|
Post by Admin on Mar 12, 2019 11:40:57 GMT
Hello, I'm wondering if I have a bad controller. Measured open voltage on the panel leads is 43 volts. When attached to controller voltage always reads battery voltage 12-13v. Panels symbol shows daylight and moon symbols but never turns on panel charge light or records charge amp hours, ever. Time to call service? Have you measured the individual panel VOC and ISC to see if there is anything wrong with particular panel? If you've never seen it charge there is a possibility that you have the cables reversed at the panel input. -Renogy Team
|
|