Post by jcmontana on Aug 28, 2018 1:59:09 GMT
I want to put a circuit breaker on my solar panel wires before they enter the controller in case I have to work on something down stream from their, like disconnecting the battery. Do I need to put a circuit breaker on both positive and negative solar panel wires or just the positive wire or just the negative wire? thanks
|
|
|
Post by jcmontana on Aug 28, 2018 2:03:35 GMT
I am running three 100 w eclipse renolgy panels and a 40amp controller, the circuit breaker I would get would also be a fused, resettable circuit breaker,,,,what size fused breaker should I get?
|
|
|
Post by bupkis on Aug 28, 2018 2:09:49 GMT
Just on the + side. 3 100 w eclispe in series, max fuse 10A see the sticker on the back!
|
|
|
Post by tattoo on Aug 28, 2018 2:15:05 GMT
Do I need to put a circuit breaker on both positive and negative solar panel wires or just the positive wire or just the negative wire? thanks
Just on the Pos+, no need putting one on the neg- side......
|
|
|
Post by jcmontana on Aug 28, 2018 2:27:00 GMT
awesome, thanks folks
|
|
|
Post by tattoo on Aug 28, 2018 12:12:07 GMT
|
|